Texas275 ![]() Supporter of TheAMCForum ![]() ![]() Joined: Dec/18/2013 Location: Forney, Tx Status: Offline Points: 401 |
![]() ![]() ![]() ![]() ![]() Posted: May/05/2020 at 8:31pm |
In need some help with my add on AC/Heat. I picked up a working used Sanden Compressor, used clean condenser, new dryer, new hoses, new evaporator/heat unit. Since the compressor was used I drained and refilled the oil according to Sanden specs. Everything connected and working, but I cant get it to cool to any lower than 60 degrees at the vent. Heat not on. I found no leaks, it held a vacuum for 3 weeks before I charged it. No noise from the compressor, engages fine when powered on and spins like it should.
When I hook up the gauges and I get 80 psi static on both gauges at 80 degree ambient temp. When its running, on high, the Low Side gauge is at 95 psi, and the High Side is at 90 psi. Looking at the sight glass on the gauges it looks pretty frothy, like its got a lot of air in the system. According to the charts the Low should be 40-50 psi and the High should be 175-210 psi. So what am I missing? I don't have a problem evacuating and recharging, If I need to replace something I can do that, I'm just kind of stuck as to my next step. ![]() Any help would be greatly appreciated, Tom
Edited by Texas275 - May/17/2020 at 4:29pm |
|
![]() |
|
Heavy 488 ![]() AMC Addicted ![]() Joined: Apr/27/2019 Location: Melmac Status: Offline Points: 1731 |
![]() ![]() ![]() ![]() ![]() |
Expansion valve?
|
|
![]() |
|
Texas275 ![]() Supporter of TheAMCForum ![]() ![]() Joined: Dec/18/2013 Location: Forney, Tx Status: Offline Points: 401 |
![]() ![]() ![]() ![]() ![]() |
Its is new with the evap/heater. Is there a way to test it, before I just buy one and put it on?
|
|
![]() |
|
Heavy 488 ![]() AMC Addicted ![]() Joined: Apr/27/2019 Location: Melmac Status: Offline Points: 1731 |
![]() ![]() ![]() ![]() ![]() |
an actual method to test I don't know. you don't really have much of any pressure differential which to me says it doesn't work.
Edited by Heavy 488 - May/05/2020 at 10:08pm |
|
![]() |
|
Texas275 ![]() Supporter of TheAMCForum ![]() ![]() Joined: Dec/18/2013 Location: Forney, Tx Status: Offline Points: 401 |
![]() ![]() ![]() ![]() ![]() |
Sounds like a plan. They are cheap and easy to get to. I'll see if I can pick one up locally tomorrow. If not, I'm sure amazon has one. Thanks for the jumping off point.
Tom
|
|
![]() |
|
motorhead_1 ![]() AMC Addicted ![]() ![]() Joined: Apr/16/2014 Location: AZ Status: Offline Points: 641 |
![]() ![]() ![]() ![]() ![]() |
wrong expansion valve. R12 and 134 should be different as the freon molecules are different sizes.
will they interchange, sure, but won't be as effective. i think your problem lies elsewhere. compressor valves likely
|
|
69 SC/Rambler tribute with 401/th400, 68 Rebel SST, 79 Concord 360 v8 wagon, 66 F100 460/c6, 88 Merkur Xr4Ti, 71 Jaguar XJ6 ls1 swap
|
|
![]() |
|
6768rogues ![]() AMC Addicted ![]() ![]() Joined: Jul/03/2007 Location: United States Status: Offline Points: 5644 |
![]() ![]() ![]() ![]() ![]() |
I suspect the used compressor. You have neither suction nor pressure. Is it R134A? If so, ignore the sight glass, it only works with R12. I don’t think it is your problem but did you charge into the vacuum? When it is working the high side should not be over twice ambient plus 80 degrees.
Edited by 6768rogues - May/05/2020 at 11:16pm |
|
Content intended for mature audiences. If you experience nausea or diarrhea, stop reading and seek medical attention.
Located near Rochester, NY |
|
![]() |
|
Texas275 ![]() Supporter of TheAMCForum ![]() ![]() Joined: Dec/18/2013 Location: Forney, Tx Status: Offline Points: 401 |
![]() ![]() ![]() ![]() ![]() |
It is a 134 evap system so I figure it is a 134 expansion valve. When I charged it initially it held vacuum for 3 three weeks before charging. I charged it with the vacuum pulled. It took it a while but it pulled all the 134 in. That was about a month ago. It was down into the 40 degree range at the vent. But now it won’t get any lower than 60 at the vent.
|
|
![]() |
|
Heavy 488 ![]() AMC Addicted ![]() Joined: Apr/27/2019 Location: Melmac Status: Offline Points: 1731 |
![]() ![]() ![]() ![]() ![]() |
what's the temp coming into the evaporator? |
|
![]() |
|
Mopar_guy ![]() Supporter of TheAMCForum ![]() ![]() Joined: Jun/07/2009 Location: Ohio Status: Offline Points: 3177 |
![]() ![]() ![]() ![]() ![]() |
Is the rest of the system stock or aftermarket? The problem is withe the pressure differential - there's not enough of it. Expansion valve is the #1 suspect.
|
|
![]() |